Mike,
WRT your hooking up your batts. First, were all the circuit breakers turned
off? (Hopefully!) Was your battery switch on batt #1, batt #2, Both, or
None. I suspect it was on “both”. Or do you have a battery switch?
Clearly, you should not hook up your batts in series, as your post states.
Your equip is made to work at nominally 12 volts, hook the 2 batts up in
series and you’ve got 24 volts - obviously too much. I expect your boat is
wired to let each batt drive your electrical load, or the batts can be operated
in parallel (not series) so that they both drive the electrical load. My
assumption below is that you've got a battery switch that lets you use batt #1,
#2, Both, or None. If you don't have a batt switch, and it wasn't on Both,
ignore the following.
I suspect you really hooked them up so that the + terminal of one batt
connected to the - terminal of the other, and the - terminal of 1 to the +
terminal of the other. You can do that by connecting one of the 2 batteries
backwards. It’s called a disaster. Your son is lucky he didn't get a face full of
acid from those batts while he was disconnecting them. Something in your
wiring limited the current, which is probably the smoking wire(s).
If I’m right (i.e. your circuit breakers were off, you have a batt switch,
and one batt was installed backward), your principle damage, apart from the
stress on your batts, might be to the wiring from the batts to the main power
switch ( #1, #2, both, none) and/or that switch. Disconnect all wires from
your batts. Put the main power switch on “both” and use a multimeter to
measure the resistance between the end of the positive leads on each batts, it
should be a short (zero Ohms, or some very small number). Do the same thing
with the resistance between the ends of the neg leads, again should be a short.
If either measurement reads any substantial resistance, you’ve got a
problem. You’ll have to change the wiring to the batt switch and/or the batt
switch. Get back to us if you find there is a problem.
You may, or may not, have disconnected in time. The Ohm meter will tell you
if you still have wiring left.
But the above is all about the continuity of the basic wiring. I suggest
you examine the insulation on those wires and the switch also, the insulation
may have melted or burned. If you've got melted or fried insulation, it's an
accident waiting to happen so you should likely change those wires regardless
of their continuity.
Good luck.
Dave